NBC foam plastic provisions
Part 3 and Part 9 of the NBC set distinct foam plastic protection requirements depending on building scope.
Canadian building code question
Foam plastic insulation in Canada must be separated from interior spaces by an approved thermal barrier unless the assembly qualifies for a specific exception, and exterior use requires verified flame-spread and fire-propagation performance under the relevant code provisions.
Foam plastics — including expanded polystyrene, extruded polystyrene, polyurethane, and polyisocyanurate — are excellent insulators but flammable. The code therefore requires layered protection, and the details of acceptable thermal barriers and exposed-foam exceptions are where designs frequently get tripped up.
Part 3 and Part 9 of the NBC set distinct foam plastic protection requirements depending on building scope.
Foam plastic used outside of fire-resistance-rated assemblies requires CAN/ULC-S134 or similar verified fire performance.
Foam plastic provisions are among the more uniformly adopted parts of the NBC across provinces.
Only in specific conditions and assemblies allowed by the code; otherwise an approved thermal barrier is required.
Typically 12.7 mm gypsum board or an assembly tested to provide equivalent fire resistance for the foam plastic involved.
Yes. Exterior use commonly requires CAN/ULC-S134 testing or other verified flame-spread and fire-propagation performance.