National baseline
Start with the NBC table matching fire resistance ratings to required fire-protection ratings for closures, then verify opening size limits.
Canadian building code question
Openings in fire separations and fire walls must be protected with fire-protection-rated closures (doors, shutters, wired glass, or fire-rated glazing) with ratings that correspond to the fire resistance rating of the assembly. The required closure rating is typically a fraction of the assembly rating, and additional requirements apply for self-closing, latching, and smoke sealing.
Opening protection is the complement to fire separation construction — a fire-rated wall is only as effective as its weakest opening. The code specifies closure ratings, maximum opening sizes, self-closing and latching requirements, and smoke-seal provisions that must be matched to each fire separation. This is one of the most complex areas of fire protection compliance.
Start with the NBC table matching fire resistance ratings to required fire-protection ratings for closures, then verify opening size limits.
Some provinces amend closure rating requirements or add provisions for specific occupancy types.
ULC standards for fire doors, fire shutters, and fire-rated glazing define testing and labelling requirements that must be matched to the code provisions.
The code specifies the relationship between assembly ratings and closure ratings in a table. The required closure rating for a 1-hour separation depends on the assembly type. Verify the specific provision.
Yes, but the glazing must meet the fire-protection rating for the separation and comply with maximum area limits. Fire-rated glazing is different from fire-resistance-rated glazing — verify which is required.
Fire doors can be held open only with hold-open devices that release automatically upon activation of the fire alarm or detection system. Propping doors open with wedges or other non-automatic devices is not permitted.